懒得说 2024-10-28 08:17 00 [回复]举报

GB55037-2022.3.4.5.4 消防车道坡度不大于10%

潘天坤 2024-10-29 13:18 00 [回复]举报

建筑防火通用规范GB55037第3.4.5条规定:消防车道或兼作消防车道的道路的坡度应满足消防车满载时正常通行的要求,且不应大于10%;如果同时兼作消防救援场地的消防车道,坡度尚应满足消防车停靠和消防救援作业的要求

建筑设计防火规范GB50016第7.1.8条规定:消防车道的坡度不宜大于8%

建筑防火通用规范GB55037配套实施指南提到:消防车道的坡度应满足消防车满载时正常通行的要求,一般按照不大于8%考虑,最大坡度不应大于10%。当建筑允许不设置专用的消防救援场地,而直接利用消防车道开展灭火救援时,该范围内的道路坡度不能影响消防车展开后的稳定和安全作业,一般不应大于3%


云中飞翔 2024-12-01 20:55 00 [回复]举报

单纯的消防车道坡度不大于10%,兼做消防救援登高作业场地的部分不大于3%。