气体灭火系统钢瓶年检问题

气体灭火配备了七氟丙烷钢瓶,这个气瓶设备是否需要年检,多久年检一次

渔夫 | 2021-04-09 10:27
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 4

黄辉 2021-04-09 11:09 00 [回复]举报

参考北京地标:

https://gf.1190119.com/article-36367.htm


 保养方法:
    a) 保养前应根据设计图纸等资料,仔细核对防护区、瓶组、启动瓶、控制装置、触发装置和启动按钮、模块等组件的标识与逻辑位置的对应关系,防止误操作;
    b) 当保养工作可能会造成误动作系统时,应采取插保险销、止动销或者断开控制线等措施后方可进行。维修保养后应将设备复原,确保系统进入准工作状态;
    c) 盛装下列气体的钢制无缝气瓶,自灭火剂充装之日起,每满五年的前一个月,应委托特种设备检验机构对气瓶及容器阀检验1次,应符合GB 13004、GB 25972的相关规定,水压试验压力(TP) 可参照表2 确定,取得合格的检验报告后方可继续使用;

表2 气体灭火系统钢制无缝气瓶的压力值
表2 气体灭火系统钢制无缝气瓶的压力值
   

d) 盛装下列气体的钢制焊接压力容器或气瓶,自灭火剂充装之日起,每满三年的前一个月,应委托特种设备检验机构对气瓶及容器阀检验1次,应符合GB 13075、TSG R0004的相关规定,取得合格的检验报告后,由具备灭火剂充装资质的机构充装符合强制性产品认证要求的灭火剂,其中压力容器水压强度试验应为相应系统最大工作压力的1.5倍,水压试验压力(TP)可参照表3确定;

表3 气体灭火系统钢制焊接压力储罐或气瓶的压力值
表3 气体灭火系统钢制焊接压力储罐或气瓶的压力值
   

e) 盛装驱动气体的气瓶自灭火剂充装之日起,每满五年的前一个月,应委托气瓶检验机构对气瓶及容器阀检验1次,气瓶检验及水压试验方法应符合GB 13004、GB 25972的相关规定,水压强度试验压力(TP)应为25.8MPa,取得合格检验报告后,由具备灭火剂充装资质的机构充装符合强制性产品认证要求的驱动气体,其中压力容器水压强度试验应为相应系统最大工作压力的1.5倍;
    f) 低压二氧化碳灭火系统贮存装置的液位计显示灭火剂损失超过10%,应由具备气瓶充装资质的机构充装符合强制性产品认证要求的二氧化碳灭火剂。

消防人说消防   回复: 黄辉2023-05-29 12:26

出处可以告知一下吗?


0    0 [回复]举报

黄辉   回复: 消防人说消防2023-05-30 09:16

0    0 [回复]举报

消防网友73006 2021-04-12 07:48 00 [回复]举报

启动气体瓶5年,七氟丙烷瓶组3年