请问这两条联动公式代表什么意思?

请问这两条联动公式代表什么意思?



消防资讯 | 2024-11-21 10:15
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

浮士德 2024-11-21 10:40 20 [回复]举报

第一条:两个各类型探测器或1个探测器加1个手报按钮或两个手报按钮,无延时启动声光警报器。

第二条:1个消火栓按钮无延时直接启动消火栓泵。

我头发贼黑   回复: 浮士德2024-11-21 13:58

第一条还要同回路,或者同防火分区&&&

1    0 [回复]举报