消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

已有住宅建筑电梯前室防火门可否由常闭式改成常开式

已有住宅建筑电梯前室防火门可否由常闭式改成常开式?有没有法律依据,因原有设计为常闭式防火门,业主经常用物体阻挡或损坏常闭式防火门,想将其改成常开式防火门。

我不是顽童 | 2025-03-31 15:28
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

EHS专家-DL 2025-03-31 17:30 10 [回复]举报

一、‌法律可行性分析

  1. 《建筑设计防火规范》的适用性
    根据《建筑设计防火规范》GB50016-2014(2018年版)第6.5.1条,‌常开式防火门允许设置在人员通行频繁的区域‌(如住宅电梯前室),但需满足以下条件:

    • 火灾时自动关闭功能‌:通过消防联动控制系统实现火灾信号触发闭门器关闭‌;
    • 状态监控功能‌:门的状态(开启/关闭)需反馈至消防控制室‌。

    若原有设计为常闭式防火门,‌在满足上述技术条件的前提下,可申请改为常开式‌‌。

  2. 《民法典》与物业管理规定

    • 改动涉及共有部分(如电梯前室)时,需经‌专有部分面积占比2/3以上且人数占比2/3以上的业主参与表决,并经参与表决业主的3/4同意‌‌;
    • 若改动影响其他业主权益(如占用疏散通道),可能违反《民法典》第272条“不得损害其他业主合法权益”的规定‌。

二、‌实施流程与要求

  1. 技术方案申报

    • 委托具备消防设计资质的单位编制‌防火门改造方案‌,明确联动控制逻辑、闭门器选型及信号反馈方式‌;
    • 向属地住建部门或消防机构提交‌消防设计变更申请‌,附设计图纸、联动控制说明等材料‌。
  2. 施工与验收

    • 施工需由具备消防设施工程专业承包资质的单位实施,确保闭门器、监控模块等符合《防火门监控器》GB29364标准‌;
    • 改造完成后,需通过‌消防验收备案‌,由消防部门核查联动关闭功能及状态反馈有效性‌。

三、‌法律风险提示

  1. 擅自改动的后果

    • 若未履行审批程序,可能被认定为“擅自停用消防设施”,依据《消防法》第60条处以‌5000-5万元罚款(单位)或警告/500元以下罚款(个人)‌‌;
    • 因改动导致火灾时人员疏散受阻,相关责任人需承担‌民事赔偿甚至刑事责任‌‌。
  2. 日常管理义务

    • 物业或业委会应加强巡查,防止常开式防火门被违规固定开启,否则仍可能被认定为“占用疏散通道”而受罚‌。

综合建议

  1. 优先完善管理措施‌:通过增设警示标识、加强业主教育减少人为破坏常闭门行为‌;
  2. 确需改造时‌:严格按规范要求完成设计审批、施工及验收流程,避免法律风险‌

(注:属地消防部门对规范执行可能存在差异,建议提前咨询确认‌。)

胡胡203 2025-04-01 17:33 00 [回复]举报

建筑设计防火规范6.4.2条文解释

通向封闭楼梯间的门,正常情况下需采用乙级防火门。在实际使用过程中,楼梯间出入口的门常因采用常闭防火门而致闭门器经常损坏,使门无法在火灾时自动关闭。因此,对于有人员经常出入的楼梯间门,要尽量采用常开防火门。

关闭

关闭

手机APP下载