消防控制室和建筑之间的乙级防火门开启朝向问题

养老院消防控制室和养老场所在同一建筑内,之间采用乙级防火门进行防火分隔,此门是否可以向控制室内部开启?控制室还有一个直通室外的门。

watterfile | 2025-04-13 07:59
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

西湾子消防小能手 2025-04-14 09:03 00 [回复]举报

直通室外的门是向外开启,没有要求是否安装乙级防火门,消控室通往室内的防火门是向建筑内方向开启的,防火门不能低于乙级,如设有人防需要安装甲级防火门。

消防人说消防 2025-04-14 10:01 00 [回复]举报

根据《建筑设计防火规范》 GB50016-2014(2018年版)6.2.7消防控制室和其他设备房开向建筑内的门应采用乙级防火门。

6.4.11 建筑内的疏散门应符合下列规定:     1 民用建筑和厂房的疏散门,应采用向疏散方向开启的平开门,不应采用推拉门、卷帘门、吊门、转门和折叠门。除甲、乙类生产车间外,人数不超过60人且每樘门的平均疏散人数不超过30人的房间,其疏散门的开启方向不限

但是根据你的表述,如该乙级防火门仅作为防火分隔,此门可向消防控制室内部开启。


hnlyplszq 2025-04-15 10:14 10 [回复]举报

《民用建筑电气设计标准》GB51348-2019第23.4.2条,表中消防控制室应为甲级防火门,向外开启。

李勤 2025-04-15 12:32 00 [回复]举报