消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

请问火灾报警按钮必须有电话插孔通话功能吗?谢谢

请问火灾报警按钮必须有电话插孔通话功能吗?谢谢

雨中行 | 2025-04-29 05:38
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 5

小唐12321 2025-04-29 09:01 00 [回复]举报

不是必须,现实中有的大部分也不能通话,这功能不实用。

消防网友68723 2025-04-29 09:07 00 [回复]举报

设有手动火灾报警按钮或消火栓按钮等处,宜设置电话插孔,并宜选择带有电话插孔的手动火灾报警按钮。

EHS专家-DL 2025-04-29 12:07 00 [回复]举报

《火灾自动报警系统设计规范》(GB 50116)‌‌第6.7.4条‌: 设有手动火灾报警按钮或消火栓按钮等处,设置电话插孔,并宜选择带有电话插孔的手动火灾报警按钮。可见不是必须。消防水泵房、防排烟机房等需联动控制的设备机房附近,避难层、大型综合体出入口等关键疏散节点最好设置‌带电话插孔型手动火灾报警按钮。

潘天坤 2025-04-29 12:14 00 [回复]举报

规范是宜设置电话插孔,并宜选择带有电话插孔的手动火灾报警按钮。建议尽量满足



李勤 2025-05-07 13:46 00 [回复]举报

关闭

关闭

手机APP下载