《建筑防火通用规范》GB55037-2022中

《建筑防火通用规范》GB55037-2022中废止了消防车道宽度高度(4*4)要求,只是要求净宽度和净空高度应满足消防车安全、快速通行的要求;请问什么情况下才能满足安全、快速同行,有没有其它规范对此高度、宽度做出明确要求。

陆海空 | 2025-06-06 14:50
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

EHS专家-DL 2025-06-06 16:05 00 [回复]举报

一般普通建筑按4.0×4.0m设计,工业/特殊建筑按5.0×5.0m甚至更大设计。GB55037-2022中废止了消防车道宽度高度(4*4)要求,而改为“消防车道或兼做消防车道的道路应符合下列规定:1道路的净宽度和净高度应满足消防车安全、快速通行的要求”,鉴于现在举高消防车、机场主力泡沫车等都超过了4m,所以消防车道宜宽不宜窄,如果消防道路还有运输的功能,道路运输的规范也是还要执行。

牛丫头消防课堂 2025-06-06 19:17 00 [回复]举报

《建筑防火通用规范》没有规定的参数,继续看《建筑设计防火规范》 GB50016-2014(2018年版)第7.1节

李勤 2025-06-09 08:02 00 [回复]举报