消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

两个防火分区互相借用安全出口

住宅建筑地下一层储藏室面积超过500㎡,设置了两个防火分区每个防火分区一个安全出口,然后在中间防火墙上设置甲级防火门,两个防火分区相互借用安全出口,这样规范允许吗,如果可以这个借用的疏散宽度怎么计算。

消防游客 | 2025-06-13 22:26
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

牛丫头消防课堂 2025-06-14 11:55 00 [回复]举报

第一,规范并没有说不允许互相借用,所以是可以互相借用的。

第二,借用的时候一定要分别借用,也就是说至少是两樘甲级防火门,各自走各自的,和它的疏散方向相配合。

第三,借用的宽度分别按照不超过本防火分区需要的疏散宽度的30%来控制。

第四,还要考虑火灾时的联动逻辑,按照《消防应急照明和疏散指示系统技术标准》 GB51309-2018第3.1.4 条、第5.4.7条,做好联动逻辑,区分相邻防火分区是否可借用,设置“禁止入内/安全出口“标识;

第五,考虑好安全出口附近的这些灯具选型,要求能改变方向的。


消防游客   回复: 牛丫头消防课堂2025-06-15 10:17

他们只在中间防火墙上安装了一个常开的甲级防火门,然后两个防火分区通过这一个常开防火门进行联通,这样应该不可以吧。

0    0 [回复]举报

牛丫头消防课堂   回复: 消防游客2025-06-16 10:11

这样做不正确

0    0 [回复]举报

LHH2737 2025-06-14 14:56 00 [回复]举报

可以,这种做法起到两个作用;1、解决安全出口数量不足的问题;2、解决疏散距离不足的问题

但是注意,这种做法是不增加疏散宽度的,便于理解可按借用0.1m考虑,不然要变成左脚踩右脚上天了

罗马苏丹 2025-06-14 18:08 00 [回复]举报

可以的,可以看看建筑设计防火规范的5.5.9条,讲的非常清楚

李勤 2025-06-16 08:00 00 [回复]举报

借用的宽度分别按照不超过本防火分区需要的疏散宽度的30%,且a借用b的宽度,b的宽度要满足(b+a借用部分的宽度),反之一样。

关闭

关闭

手机APP下载