消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

采用耐火电缆的消防供电线路,明敷时,是否需要套封闭式防火线槽

如题:

见2018版建筑防火规范:

对于耐火电缆没有明确说明,如果不是穿电缆井、沟时(如在车间内),是否需要采用封闭式防火线槽。

望解答,谢谢!

Ruages | 2021-08-27 15:15
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

杨江峰 2021-08-28 18:42 00 [回复]举报

这说的还不清楚?耐火电缆敷设在电缆井、沟可不穿管;矿物绝缘电缆可明敷。

关闭

关闭

手机APP下载