消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

关于同一厂区内不同厂房内消防控制室是否可以合并的问题

汽车制造企业,同一厂区内不同设置消防控制室,如总装车间一个涂装车间一个,考虑到省人需求,是否可将两个消防控制室合并,合并是否有具体的距离要求。


先说下个人理解,这两个厂房设计备案报审的时候图纸中都是存在消防控制室的,合并的话势必要改变图纸内容,是否可行,是否需要重新报审,报审是够能够通过?

神策 | 2021-12-21 08:35
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

许迅 2021-12-21 16:31 00 [回复]举报

合并的话要按总分控制室去设置,信号要能传输和控制。报审具体要看住建部门,技术上问题不大。就是麻烦。

剑胆琴心 2022-01-11 08:46 00 [回复]举报

火灾自动报警系统分为三种形式,一种是区域火灾报警系统、第二种是集中火灾报警系统、第三种是控制中心火灾报警系统,按照文中的表述你所描述应该是在图纸设计中总装车间和涂装车间分别设置了第二种集中火灾报警系统,综合考虑你可以采用第三种报警系统模式,但是需要确定哪一个是主控室,主控室可以实现对所有分控室报警设备及联动设备的显示及联动控制,而分控室只能对自身所监控的报警设施实现状态显示及联动控制。后期厂企扩建新建工程都可以接入该控制中心报警系统。供参考。

关闭

关闭

手机APP下载