建设的仓库由于屋顶未做隔热层,喷淋头距离屋顶的距离是10-15CM,夏天炎热屋顶铁皮温度较高,使68度的喷淋头经常破裂。公司安装了诱导风机,但是治标不治本,还是会经常破裂。仓库为1层的钢构铁皮棚,就目前的这种情况,按照什么标准可以换成93度的喷淋头呢?

青城 | 2022-01-24 09:02
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0

回答 | 4

ROY 2022-01-24 17:51 00 [回复]举报

根据自动喷水灭火系统设计规范第6.1.2 ,闭式系统的洒水喷头,其公称动作温度宜高于环境最高温度30℃。但是你们这种库房的最高环境温度应该是无法达到38℃以上,可能并不能更改高温喷头。


此外,如屋顶温度可达到60℃以上,你们库房夏季的火灾风险可能有点大,应该慎重考虑从根本解决问题。

刘丽波 2022-01-24 19:00 00 [回复]举报

《自喷规》6.1.2 闭式系统的洒水喷头,其公称动作温度宜高于环境最高温度30℃。采用较高动作温度的喷头,冬季时反应不灵敏,如上部温度长期过高,是否考虑改为干式或预作用系统?

ROY   回复: 刘丽波2022-01-26 08:59

预作用系统仍不能解决喷头破裂的问题,可以减少误喷水造成的损失。

干式系统对于解决问题此问题并无帮助,除非发生报警后可以立即赶往现场进行处置。

如考虑更换报警阀,可以对仓库区域单独配置开式喷头,使用雨淋系统。

1    0 [回复]举报

消防网友34346 2022-01-27 14:26 00 [回复]举报

如果空间大,满足水炮要求的话是否改成水炮