一类高层公寓,一、二层商业的疏散楼梯是否需要设置防烟楼梯间,一二层与上面楼层独立疏散,现改造为旅馆,土建设置的为敞开楼梯间,2000年造的老房子,商店规范已经废止,没找到其他相关条文

消防网友25595 | 2022-02-24 08:51
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

刘丽波 2022-02-24 09:12 10 [回复]举报

整体是一类公建,主体下疏散楼梯形式同主体,裙房部分可以考虑采用封闭楼梯间。现行规范无论是商业还是旅馆都不能采用敞开楼梯间的形式。

陈曲 2022-02-25 12:36 00 [回复]举报

这个刚才回答错了 不知道怎么撤销 