消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

厂房内的观光走道隔墙怎么处理?

丙类厂房内,有一条观光走道请问观光走道上隔墙上面开窗要满足什么要求?

防火间距 | 2022-03-02 02:00
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

陈曲 2022-03-02 08:36 00 [回复]举报

个人建议一般厂房参考 建规3.3.5 办公室、休息室设置在丙类厂房内时,应采用耐火极限不低于2.50h的防火隔墙和1.00h的楼板与其他部位分隔,并应至少设置1个独立的安全出口。如隔墙上需开设相互连通的门时,应采用乙级防火门。


hbedsn 2022-03-02 17:11 00 [回复]举报


先确定厂房的耐火等级,根据建规表“3.2.1”确定走廊两侧墙体耐火极限,再确定墙上防火窗或玻璃隔断的耐火极限。

关闭

关闭

手机APP下载