水喷雾系统的稳压泵一直有气蚀现象

我们是钢铁企业,按照钢铁防火规范地下液压站,润滑站都安装了水喷雾系统。系统的设计压力跟流量是0.32/750,稳压泵的最大工作压力是0.6。现在稳压泵的启停泵压力是0.35-0.45,这个值符合规范吗?稳压泵启动一直存在气蚀现象,已经排过四次空气了。厂家给的回复是新泵运行一段时间就没事了。现在有几个雨淋阀组的供水侧压力比控制腔压力大了0.1。稳压泵正常启动一直有空气打不上压,又存在压差,会不会压差太大,阀瓣会被冲开误喷

消防网友57400 | 2022-04-12 20:52
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

老衲 2022-04-15 12:11 10 [回复]举报

看你水喷雾用于防护冷却还是灭火,如果是灭火一般0.35-0.8,如果是防护冷却一般0.2-0.6,稳压泵存在气蚀,看泵本体的密封或是否有缺陷,或者看进水是否存在问题。启动水泵误喷的情况一般不会,水喷雾启动应该是烟感手报给控制器信号再来启动阀与水泵

消防网友57400   回复: 老衲2022-04-30 10:30

我们的水喷雾是灭火的,用的火焰探测器。稳压泵的吸水管确实有点细,但是也不排除泵的密封有问题。现在疫情期间,厂家也过不来

0    0 [回复]举报