请教老师,消防给水及消火栓系统技术规范 GB50974的问题

请教老师,消防给水及消火栓系统技术规范 GB50974—2014

发布前,建筑消防水系统按哪个标准组织设计、施工、验收?

目前,面临一个高层建筑高位水箱容积的问题了因为是老建筑,

无法查到当时的配置是否符合规范要求。谢谢!

消防网友30777 | 2022-08-09 22:46
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 8

周家斌 2022-08-10 08:23 00 [回复]举报

建筑设计防火规范 GB50016-20068.4.4 设置常高压给水系统并能保证最不利点消火栓和自动喷水灭火系统等的水量和水压的建筑物,或设置干式消防竖管的建筑物,可不设置消防水箱。   设置临时高压给水系统的建筑物应设置消防水箱(包括气压水罐、水塔、分区给水系统的分区水箱)。消防水箱的设置应符合下列规定:   1 重力自流的消防水箱应设置在建筑的最高部位;   2 消防水箱应储存10min的消防用水量。当室内消防用水量小于等于25L/s,经计算消防水箱所需消防储水量大于12m³时,仍可采用12m³;当室内消防用水量大于25L/s,经计算消防水箱所需消防储水量大于18m³时,仍可采用18m³;   3 消防用水与其它用水合用的水箱应采取消防用水不作他用的技术措施;   4 发生火灾后,由消防水泵供给的消防用水不应进入消防水箱;   5 消防水箱可分区设置。

消防网友30777   回复: 周家斌2022-08-12 19:11

谢谢老师

0    0 [回复]举报

消防网友73633 2022-08-10 08:58 00 [回复]举报

《高层民用建筑没计防火规范》GB 50045—95(2001年版)7.4.7.1 高位消防水箱的消防储水量,一类公共建筑不应小于18m3;二类公共建筑和一类居住建筑不应小于12m3;二类居住建筑不应小于6.00m3

消防网友30777   回复: 消防网友736332022-08-12 19:11

谢谢您

0    0 [回复]举报

南明离火 2022-08-10 14:41 00 [回复]举报

看是否有验收合格意见书,有就合格,没有的话再分情况

消防网友30777   回复: 南明离火2022-08-12 19:12

谢谢您的提醒

0    0 [回复]举报

消防黄河 2022-08-10 21:05 00 [回复]举报

老《高规》

消防网友30777   回复: 消防黄河2022-08-12 19:12

谢谢您

0    0 [回复]举报