消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

排烟口设置

地下车库储烟仓的空间是根据梁来确定的吗?如果排烟风管朝下开排烟口低于梁底高度是不是就属于不在储烟仓以内?是不是违反规范了?有没有相关条文?

请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

张牙舞爪的张 2022-12-07 09:17 00 [回复]举报

是的。前提是你的梁大于净空高度的百分之十且大于500mm。《烟规》4.4.11

消防黄河 2022-12-07 22:45 120 [回复]举报

1.不一定,梁是划分防烟分区的一种形式,用梁划分时对其突出顶板高度有要求。2.不一定了,应对照储烟仓判断。以上两点清楚了,3和4就解决了。

和德 2022-12-09 08:53 00 [回复]举报

如果梁的高度满足储烟仓厚度就行,排烟口必须在储烟仓内,否则就设置挡烟垂壁,保证排烟口在储烟仓内。

米米果果 2022-12-15 16:58 00 [回复]举报

结构梁可以用来划分防烟分区,可作为防烟分隔设施的一部分。根据烟规说明,储烟仓=车库净高—设计清晰高度,而清晰高度需要根据公式算出。建议可以看下烟规图集,把储烟仓的概念高清楚。对于底下车库,我们一般是采用结构梁+挡烟垂壁的组合来进行防烟分隔。至于排烟口能不能开在风管底部需要看车库净高和你计算出的烟层厚度(db)来定。

关闭

关闭

手机APP下载