消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

附设在建筑内的变配电室直接用玻璃幕墙,那耐火极限有要求么?

附设在建筑内的变配电室等,应采用耐火极限不低于2.00h的防火隔墙和1.50h的楼板与其他部位分隔。(6.2.7)

那我变配电室直接用玻璃幕墙跟外界连接呢?规范怎么解读?

徐州消防 | 2023-04-10 11:45
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

消防老胡 2023-04-10 12:22 00 [回复]举报

防火玻璃按耐火极限分5个等级:0.5h、1.00h、1.50h、2.00h、3.00h。防火隔墙要达到耐火极限≮2.0h,就需要选择耐火极限≮2.0h的A型(耐火完整性和耐火隔热性均符合要求)防火玻璃,与之配套的防火隔墙选择的构造柱及框料也均要求完整性和隔热性≮2.0h,还要有一定的牢固性。在此隔墙上开洞就直接选用符合规范的甲级防火门即可。如果有桥架穿越按照同样要求做防火封堵即可。

关闭

关闭

手机APP下载