GB55037-2022标准删除条款的疑问

新发布的GB55037 -《建筑防火通用规范》 中明确删除的条款,比如3.3.1、3.4.1, 可是在新版通用规范中并没有重新明确相关内容。那比如原版规范中比如3.3.1关于厂房的层数和每个防火分区的最大允许建筑面积、3.4.1厂房之间及与乙、丙、丁、戊类仓库、民用建筑等的防火间距等内容,在后续建筑设计中到底该如何确定?旧版删除的内容,在新版中没有明确的,后续工作中是否继续以旧版内容为准?

woshijmhc | 2023-04-21 17:37
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

消防老胡 2023-04-21 21:49 00 [回复]举报

因为新规是2023年6月1日期施行,目前阶段仍然按照GB50016执行。个人觉得《通规》施行后,《通规》有明确规定的按照《通规》要求严格执行,没有明确的由当地相关部门或第三方组织论证、评审(规范的的本意给了下限,没有给出上限)或者以地方规定标准确定执行。。

超点点速 2023-04-23 09:02 00 [回复]举报

按照目前(旧规范没有修改的情况下),要求看通规,参数看技术。也就是需不需要设置什么,看通规,通规上要求设置就设置,没要求就不设置。怎么设置,什么位置,大小参数,材质参数等看技术规。后期即使技术规修改了。也只是参照通规要求修订。

陈曲 2023-04-23 09:39 10 [回复]举报

通用规范有具体规定的按通规 没有明确的在新规范出来之前继续执行旧规范 通规只是删掉就旧规条文的强制性

晓明 2023-04-23 11:46 00 [回复]举报

《通规》只是取消了原《建规》的相关条款的国家强制性,具体做法、技术参数仍可依据现行规范执行。今后预计会将现行《建规》修订为推荐性标准,作为《通规》的配套标准使用。