消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

一体式水泵房-爬梯

请问各位老师:改造工程需要做水泵房,打算做一体式水泵房,他们是用检修口进入地下水泵房的,这个有规范要求么?单独的室外地埋式水泵房出口是否可以是竖向爬梯?

蝶阀 | 2023-04-23 17:19
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

消防网友78337 2023-04-24 14:57 00 [回复]举报

建筑设计防火规范 GB50016-2014(2018年版)


5.5.5 除人员密集场所外,建筑面积不大于500m²、使用人数不超过30人且埋深不大于10m的地下或半地下建筑(室),当需要设置2个安全出口时,其中一个安全出口可利用直通室外的金属竖向梯。     除歌舞娱乐放映游艺场所外,防火分区建筑面积不大于200m²的地下或半地下设备间、防火分区建筑面积不大于50m²且经常停留人数不超过15人的其他地下或半地下建筑(室),可设置1个安全出口或1部疏散楼梯。     除本规范另有规定外,建筑面积不大于200m²的地下或半地下设备间、建筑面积不大于50m²且经常停留人数不超过15人的其他地下或半地下房间,可设置1个疏散门。


6.4.6 用作丁、戊类厂房内第二安全出口的楼梯可采用金属梯,但其净宽度不应小于0.90m,倾斜角度不应大于45°。     丁、戊类高层厂房,当每层工作平台上的人数不超过2人且各层工作平台上同时工作的人数总和不超过10人时,其疏散楼梯可采用敞开楼梯或利用净宽度不小于0.90m、倾斜角度不大于60°的金属梯。


综合上两条,单独的室外地埋式水泵房,爬梯直通室外是可以的,同时要注意消防水泵房防水淹和通风问题的解决。

陈曲 2023-04-25 08:59 00 [回复]举报

不可以 金属爬梯只能用于防火分区的第二出口 

如果验收项目 过不了的 可以设置成斜梯

关闭

关闭

手机APP下载