消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

消防控制室开向建筑内的门应采用乙级防火门,那开向建筑内的窗是如何要求的?

消防控制室和其他设备房开向建筑内的门应采用乙级防火门,那消防控制室开向建筑内的窗是如何要求的?也是要求乙级吗?

富哥 | 2023-06-05 09:16
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

安洪全 2023-06-05 09:27 00 [回复]举报

答:不应低于乙级防火窗,是可以根据火通的规范推导出来的。


建筑防火通用规范 GB55037-2022


4.1.8 消防控制室的布置和防火分隔应符合下列规定:    

1 单独建造的消防控制室,耐火等级不应低于二级;   

2 附设在建筑内的消防控制室应采用防火门、防火窗、耐火极限不低于2.00h的防火隔墙和耐火极限不低于1.50h的楼板与其他部位分隔;    

3 消防控制室应位于建筑的首层或地下一层,疏散门应直通室外或安全出口;    

4 消防控制室的环境条件不应干扰或影响消防控制室内火灾报警与控制设备的正常运行;    

5 消防控制室内不应敷设或穿过与消防控制室无关的管线;    

6 消防控制室应采取防水淹、防潮、防啮齿动物等的措施。


6.4.7 下列部位的窗的耐火性能不应低于乙级防火窗的要求:    

1 歌舞娱乐放映游艺场所中房间开向走道的窗;    

2 设置在避难间或避难层中避难区对应外墙上的窗;    

3 其他要求耐火极限不低于2.00h的防火隔墙上的窗。

hnlyplszq 2023-06-05 10:28 00 [回复]举报

在《民用电气》规范中要求,消防控制室内门是甲级防火门。

关闭

关闭

手机APP下载