甲类仓库中的防火分区

甲类仓库(面积不大于防火分区最大面积)中设置有其他隔间(存储甲类物品和危废间),这些隔间与甲类仓库需要设置防火墙吗?还是分隔开即可,谢谢


隐尘 | 2023-07-06 08:53
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

安洪全 2023-07-06 14:33 10 [回复]举报

建筑防火通用规范 GB55037-2022

4.2.6 仓库内的防火分区或库房之间应采用防火墙分隔,甲、乙类库房内的防火分区或库房之间应采用无任何开口的防火墙分隔。