消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

事故排风风速

请教大家:厨房燃气的事故排风系统风道和风口的风速分别取多少合适?事故排风系统需要做消防联动吗?还是只在现场做手动控制即可?

心的自由 | 2023-07-13 10:41
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

安洪全 2023-07-13 13:34 00 [回复]举报

whale 2023-07-17 08:46 00 [回复]举报


潘天坤 2024-06-21 16:27 00 [回复]举报


管道和风口的风速可以参照民用建筑规范的平时通风要求,规范是宜字并且是平时通风

使用天然气的公共厨房的配套事故排风,一般需要设置相应的检测报警及控制系统(附近会设置可燃气体探测设备,事故通风设施与可燃气体探测设备连锁)

工业建筑的事故通风设施的相关要求:工作场所设置有有毒气体或有爆炸危险气体监测及报警装置时,事故通风装置应与报警装置连锁。
民用建筑的事故通风设施的相关要求:事故通风应根据放散物的种类,设置相应的检测报警及控制系统。

关闭

关闭

手机APP下载