关于排烟防火阀的疑惑

大家好,请教一个问题。排烟防火阀是否需要同排烟阀一样做就地1.5米按钮。一个排烟系统负担同一防火分区多个防烟分区时,排烟支管做排烟防火阀。当着火区域发生火灾,需要关闭其他防烟分区支管排烟防火阀。此时若线路故障,该排烟防火阀未及时关闭,确保烟气不蔓延,是否需手动关闭。是否可以通过钢丝绳做就地1.5米按钮,快速关闭该排烟防火阀。火灾结束通过检修口复位。请大家指导。

沐晚庭晓 | 2023-10-23 03:18
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

消防网友21314 2023-10-23 07:51 10 [回复]举报

不需要安装1.5米按钮,风口前有常闭的排烟阀需要。

阳明心 2023-10-23 08:30 10 [回复]举报

在用项目如果已经安装了常开排烟防火阀,作为后期改造,这是个办法。

沐晚庭晓   回复: 阳明心2023-10-23 09:52

谢谢

0    0 [回复]举报

周家斌 2023-10-23 08:33 10 [回复]举报

排烟支管做排烟防火阀是常开的。当着火区域发生火灾,不需要关闭其他防烟分区支管排烟防火阀的。因排烟阀(或者是排烟口)是常闭的,理论上不存在烟气蔓延的啊。

沐晚庭晓   回复: 周家斌2023-10-23 09:52

谢谢

0    0 [回复]举报

阳明心   回复: 周家斌2023-10-23 10:40

周老师高见,谢谢

0    0 [回复]举报

潘天坤 2024-06-20 00:00 00 [回复]举报

不知道市场上有没有满足要求的电动排烟防火阀产品

排烟支管上设置排烟防火阀是防止火灾通过排烟管道蔓延到其他区域,排烟防火阀具有熔断功能,达到公称动作温度会熔断,不需要设置手动操作装置。