CT室是否需要安装防火门?

现对旧房屋进行改造,设计CT室房门是需要安装防火门,但是防火门不能够防辐射,请问这要怎么处理?

lky90 | 2023-11-16 09:45
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

周家斌 2023-11-17 14:25 20 [回复]举报

不要定性为贵重精密医疗装备用房就可以啦,此处还是以防护为主。

我的是昵称 2023-11-17 16:03 00 [回复]举报

不要把防火门片面的理解成木质的或钢质的常见的形式的门。各式各样的门只要达到防火门的要求,有铭牌有证书就都是防火门。你可以去防火门的厂家那里咨询或订制防辐射的防火门。你们对旧房屋改造有没有图纸设计?有没有报住建装修办?是设备房图纸上肯定是甲级防火门。

lky90   回复: 我的是昵称2023-11-27 08:05

有图纸设计的,有报住建装修的    但是设计图纸中CT检查室的门是要装双开防火门,现CT室入口门是电动的推拉门,推拉门是防辐射的,但是消防查验说推拉门不符合要求

0    0 [回复]举报

我的是昵称   回复: lky902023-11-29 08:41

按图纸施工,不按图纸住建是验不过的。你可以先按要求装防火门。等住建验收通过后,再改回自已想安装的门。基本上都是这样操作的。这样你们的目的达到了,住建也不用担责。双赢。

0    0 [回复]举报