手动拉正压风阀联动启动相邻层正压风阀出自那条规范?

手动拉正压风阀联动启动相邻层正压风阀出自那条规范?

微明 | 2023-11-28 11:55
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 6

whale 2023-11-28 15:43 00 [回复]举报

《建筑防烟排烟系统技术标准》GB512512017

微明   回复: whale2023-11-28 21:13

这属于两点联动启动本层和相邻层,不是单独测试本层的阀,相邻层也要打开的规范来源,还是说规范没有这个要求。

0    0 [回复]举报

微明   回复: 微明2023-11-29 09:50

我们这边专家提出来的,现在没办法实现,联动编程的话一整栋楼全都会联动打开,是个连锁反应。

0    0 [回复]举报

whale   回复: 微明2023-11-29 09:54

没查到要求阀门之间联动的条文,我们这边设计应该是任意一层风口被手动启动相应风机联动启动,相邻楼层风口由消控室控制开启。

1    0 [回复]举报

潘天坤   回复: 微明2024-06-19 20:18

图集(20K607第27页)有个示图:人员开启加压送风口-输入模块通过总线反馈风口开启信号-消防联动控制器通过总线控制该防火分区内着火层及相邻上下层前室及合用前室的常闭加压送风机开启,相应防火分区的全部加压送风机启动

0    0 [回复]举报

潘天坤 2024-06-19 20:08 00 [回复]举报

手动拉阀,从图集来看属于“确认火灾”,所以符合“火灾确认后相关要求”

图集(20K607第27页)有个示图:人员开启加压送风口-输入模块通过总线反馈风口开启信号-消防联动控制器通过总线控制该防火分区内着火层及相邻上下层前室及合用前室的常闭加压送风机开启,相应防火分区的全部加压送风机启动

从规范角度来说,没有提到连锁。如果结合图集理解,将按下加压送风口执行机构认为是确认火灾,那么执行GB51251要求也是应该的。

不过这样子要求可能存在一定争议,毕竟图集不好直接当规范使用,建议按照设计要求执行