消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

地板下面的电缆层的火灾探测

为何地板下面的电缆层需要设立火灾检测探头?地板下面的空间需要做一个独立的防火分区来处理吗?按哪个条款来计算所需要设立火灾检测探头的数量呢?谢谢

消防网友84139 | 2023-12-15 12:36
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 1

卡卡拉 2023-12-26 09:56 00 [回复]举报

一、火灾自动报警系统设计规范 GB50116-2013 附录D火灾探测器的具体设置部位 第24条 敷设具有可延燃绝缘层和外护层电缆的电缆竖井、电缆夹层、电缆隧道、电缆配线桥架。

二、火灾自动报警系统设计规范 GB50116-2013  3.3.2 探测区域的划分应符合下列规定:
1 探测区域应按独立房(套)间划分。一个探测区域的面积不宜超过500㎡ ;从主要入口能看清其内部,且面积不超过1000㎡的房间,也可划为一个探测区域。

2 红外光束感烟火灾探测器和缆式线型感温火灾探测器的探测区域的长度,不宜超过100m; 空气管差温火灾探测器的探测区域长度宜为20m~100m。

三、火灾自动报警系统设计规范 GB50116-2013 5.3.3 下列场所或部位,宜选择缆式线型感温火灾探测器:
1 电缆隧道、电缆竖井、电缆夹层、电缆桥架。

关闭

关闭

手机APP下载