消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

烟感这样安装可以吗?觉得不符合要求,一直没找到规范

烟感这样安装可以吗?觉得不符合要求,一直没找到规范

张曼杰 | 2023-12-16 14:05
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


精彩评论

刘席,郑州 2023-12-17 15:20

这样安装可以,但是得按自动报警设计规范表6.2.9上控制高度

查看原文
回答 | 6

天堂鸟 2023-12-16 17:49 10 [回复]举报

可以,需满足消防明管敷设要求

yizhongdayang 2023-12-17 11:33 00 [回复]举报

除了有热屏障的屋顶,其他位置的点型探测器应吸顶安装。《火灾自动报警系统设计规范》(GB50116-2013)6.2.3、6.2.4条款均规定了在有梁顶棚、走道顶棚安装的要求。《火灾自动报警系统施工及验收标准图示》(21X505-2)中火灾探测器的安装示意图也是吸顶安装。

刘席,郑州 2023-12-17 15:20 00 [回复]举报

这样安装可以,但是得按自动报警设计规范表6.2.9上控制高度

大力水手吃菠菜 2023-12-17 15:40 00 [回复]举报

不可以,如果燃烧方式阴燃或燃烧的产烟小,错过探测器有效探测范围聚集到屋顶,会影响到报警时间从而错过初期扑灭火灾的时机。



懒得说 2023-12-17 15:48 00 [回复]举报

就看你认为哪个位置烟气浓度最高了

大司马 2023-12-18 15:50 00 [回复]举报

《自动报警规范》6.2.9,要看有没有热屏障产生。有的话可以参考以下规范

关闭

关闭

手机APP下载