消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

办公楼火灾自动报警测试,电气管道井非消防电源需要强切吗?

在一栋办公楼三层试火灾自动报警系统,三层除了电气管道井的非消防电源没有强切,别的都强切了,这个符合不符合规范要求?

Vv | 2021-01-23 19:55
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

赖峰 2021-01-27 17:29 00 [回复]举报

消防联动控制器应具有切断火灾区域及相关区域的非消防电源的功能,当需要切断正常照明时,宜在自动喷淋系统、消火栓系统动作前切断。《火灾自动报警系统设计规范 GB50116-2013》第4.10.1)

高波 2021-05-12 20:58 00 [回复]举报

不符合规范要求,电气管道井的非消防电源也应强切。目前,住宅楼户内的电源,据说不要求强切。


关闭

关闭

手机APP下载