老师您好,《建规》8.5.3条规定:建筑内长度大于20m的疏散走道应设置排烟设施,请问内走道两端开窗最长可以设计成多长?一端开窗的情况呢?两端(侧)均设置面积不小于2m2的自然排烟窗(口)是指可开启窗扇还是 指整个窗户的 面积?

消防网友73154 | 2021-01-29 13:32
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

刘丽波 2021-01-29 14:10 10 [回复]举报

执行《烟规》4.6.3-3时两侧开窗,净宽小于2.5米时,最长可以60米;执行4.6.3-4可以单侧开窗,排烟窗距防烟分区最远点不超30米。排烟窗均为有效面积,计算方法按《烟规》4.3.5执行。

郭建华 2021-01-29 15:31 00 [回复]举报

两端开窗最多可做60米,一端开窗最多可做30米。2平米自然排烟窗是指可开启扇面积,而且是指在储烟仓内的可开启扇面积。规范写的很详细,可查看规范。

郭建华 2021-01-29 15:34 00 [回复]举报

两端开窗最多可做60米,一端开窗最多可做30米。2平米自然排烟窗是指可开启扇面积,而且是指在储烟仓内的可开启扇面积。规范写的很详细,可查看规范。