防排烟竖井内径管安装有困难时怎样处理

红1127 | 2024-03-06 21:20
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 8

南明离火 2024-03-07 08:40 10 [回复]举报

设计变更,内部混凝土竖井抹光滑

GANSTER   回复: 南明离火2024-03-08 09:06

强制性条文岂能随随便便修改?土建风道的密闭性怎么保证?

0    0 [回复]举报

南明离火   回复: GANSTER2024-03-08 14:34

通用规范已经没有显示这个是强制条文了

0    0 [回复]举报

jhons   回复: 南明离火2024-03-15 16:08

通用规范所有条文都属于强条

0    0 [回复]举报

南明离火   回复: jhons2024-03-18 08:42

11.1.3 机械加压送风管道和机械排烟管道均应采用不燃性材料,且管道的内表面应光滑,管道的密闭性能应满足火灾时加压送风或排烟的要求。



表面光滑 并非一定要 金属风道

0    0 [回复]举报

潘天坤   回复: 南明离火2024-06-17 00:04

土建风道一般无法达到“内表面光滑、不漏风”,无法保证管道的密闭性能。

正文要求“内表面光滑、不漏风、”,实施指南要求“摩阻系数、气密闭性应符合系统送风和排烟要求”。

土建风道的气密闭性能不太好测试,测试也不准确,如果被提出要求证明的话,一般也无法证明。

同时烟规GB51251关于土建风道的相关要求,一般也认为还存在,一般作为非强制性条文的“应”要求。

0    0 [回复]举报

懒得说 2024-03-09 17:28 00 [回复]举报

只有适当减小截面尺寸。建筑井道内壁光滑无法保证

潘天坤 2024-06-16 23:52 00 [回复]举报

土建风道存在很多隐患,不建议这样子操作

土建风道一般也无法满足内壁光滑要求

烟规GB51251关于土建风道的相关要求,一般认为还可以当做非强制性条文提出

可以跟设计单位沟通看看,尽量满足规范相关要求