七氟丙烷的设置要求

请问一下大家,有没有规范里说明层高多少米就不能设置柜式七氟丙烷了

平心 | 2024-04-07 14:20
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 2

一半一半 2024-04-07 16:34 20 [回复]举报

防护区的面积不宜大于500m2,容积不宜大于1600m3;柜式七氟丙烷气体灭火装置主要适用于电子计算机房、配电房、变压器房、档案文库资料室、小型油库、电讯中心等小型防护区的消防保护。没有具体的空间高度要求

Designer 2024-04-08 10:02 10 [回复]举报

没有,但有防护区体积要求