消防水泵房的温湿度是多少?有国家标准规范要求吗?

还有,消防水泵控制柜,单独安装在控制室内的时候,对于温湿度是否有国家规范的要求?请指点,谢谢!

MHW | 2024-04-13 11:19
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

牛奶面包蛋 2024-04-13 14:05 00 [回复]举报

消防给水及消火栓系统技术规范 GB50974-2014 5.5.9

严寒、寒冷等冬季结冰地区采暖温度不应低于10℃,但当无人值守时不应低于5℃

未对湿度有要求。

但对消防水泵防护等级有要求

消防给水及消火栓系统技术规范 GB50974-2014 11.0.9 

消防水泵控制柜设置在专用消防水泵控制室时,其防护等级不应低于IP30;与消防水泵设置在同一空间时,其防护等级不应低于IP55。

肖同桂 2024-04-14 19:03 00 [回复]举报

消防给水及消火栓系统技术规范

lj002 2024-04-16 01:19 00 [回复]举报

1、消防水泵房温湿度无明确要求,对水泵房有机械换气要求;

2、消防水泵控制柜未放置在水泵房时要求是IP30

阿白_71xU 2024-04-16 22:25 00 [回复]举报

不低于5摄氏度