消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

只有消火栓泵是否需要设置集中报警

只有消火栓泵,是否应设置集中报警系统?

如果不设置,手动启停如何实现?

消防电话是否需要设置?

型式批准 | 2024-04-17 08:43
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 4

feisha 2024-04-18 10:52 00 [回复]举报

1、设置火灾报警系统要看建筑类别和面积,不依据配备了哪些消防设施。

2、水泵控制柜上有手动启停,也可设置单独的专线手动启停回路。

3、如果建筑不需要设置火灾报警系统,那也不需要设置消防电话。

一个呆呀 2024-04-18 11:15 00 [回复]举报

要不要报警系统具体要看那种建筑物和用途,水泵的远程启停很简单,对讲电话最好装一个

熬不牢一泡肚皮杂 2024-04-19 00:10 00 [回复]举报

不需要,之前的做法在每个消火栓箱中设按钮,作联锁启泵功能,现在不用按钮,通过低压压力开关启泵

龙蟠镖客 2024-04-19 09:06 10 [回复]举报

是否设置火灾自动报警系统看建筑使用性质及大小。

GB50116-2013中条文说明4.3.1当建筑物内无火灾自动报警系统时,消火栓按钮用导线直接引至消防泵控制箱(柜),启动消防泵。

关闭

关闭

手机APP下载