消火栓箱门材料是否可以和装修材料一致?

请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 7

phone0224 2024-06-26 08:54 20 [回复]举报

可以啊。《建筑内部装修设计防火规范》

周家斌 2024-06-26 09:30 30 [回复]举报

可以,但是标识满足要求

潘天坤 2024-06-26 11:43 30 [回复]举报

消火栓箱门四周的装修材料颜色应与消火栓箱门的颜色有明显区别,当现场无法明显区别的时候,应在消火栓箱门表面设置发光标志

建筑内部装修设计防火规范 GB50222-2017第4.0.2条规定:建筑内部消火栓箱门不应被装饰物遮掩,消火栓箱门四周的装修材料颜色应与消火栓箱门的颜色有明显区别或在消火栓箱门表面设置发光标志

消防人说消防 2024-07-02 23:08 20 [回复]举报

不可以,从消防产品的型式检验报告中可知消火栓箱的整体性和完整性是不能破坏的,图中的并非消火栓箱门。也恰恰违反了《建筑内部装修设计防火规范》4.0.2条之规定。

须尽欢 2024-07-03 09:45 10 [回复]举报

可以,我项目上很多这种情况的,说白了就是消火栓装修时包进去,这种做法是可以的,不过要在门上做消火栓明显标识,和加一个小把手。

还有一个点就是不能门中门,里面的箱体的原有门不要装。

好学先生 2024-07-17 09:43 10 [回复]举报

不可以改装消火栓箱门!消火栓箱是消防认证产品,不得私自改装,因为消火栓箱的认证文件是成套产品的认证,不得拆分。但是,装修时为了美观,可以用装修材料盖住,但要做明显标识或发光标识并方便使用。

834.1 2024-08-01 08:45 10 [回复]举报

可以