商住楼还员工宿舍

商住楼为物业所有,一楼为临街商铺,已对外出租,二楼暂未对外出租,物业能否将部分房间改员工宿舍

不想蒋道理 | 2024-08-18 08:32
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 3

LHH2737 2024-08-19 09:46 10 [回复]举报

不建议这么干,商铺不能住人,非要设宿舍的话,应按宿舍建筑设计规范5.2.2: 宿舍建筑内的宿舍功能区与其他非宿舍功能部分合建时,安全出口和疏散楼梯宜各自独立设置,并应采用防火墙及耐火极限不小于2.0h的楼板进行防火分隔。(虽然规范为宜,但条文解释说:特别是与其他人员密集的公共场所合建时,二者的安全出口和疏散楼梯不应共用)

不想蒋道理   回复: LHH27372024-08-19 14:58

一楼和二楼有单独的安全出口,没有公用

0    0 [回复]举报

西湾子消防小能手   回复: 不想蒋道理2024-08-20 08:34

只要是不和商铺公用一个楼梯或出口就可以

0    0 [回复]举报