我们超市的喷淋系统的水源是市政供水,水泵房(消防井)在地下。水泵房就看到只有一个报警阀组,怎么我们超市有三个末端试水装置呢?库房一个,厕所二个,怎么也不明白。谢谢您

阿进 | 2024-09-19 13:54
请写下您的回答回答
输入一些内容
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
字符数: 0
单词数: 0


回答 | 3

LHH2737 2024-09-19 15:51 20 [回复]举报

我猜测是因为你们超市有三个防火分区,一个湿式报警阀可以带多组水流指示器,每个防火分区有一个独立的水流指示器,按照规范每个水流指示器的末端要设置试水阀(也可以安装末端试水装置),每个湿式报警阀最远的水流指示器的最末端则安装末端试水装置

阿进   回复: LHH27372024-09-22 10:07

谢谢您!