消防资源网,实时消防资讯·消防问答·精选优秀消防专题
登录     

依据消防设施通用规范GB55036-11.3.5条是不是可以认为只要是280℃排烟防火阀关闭,就要连锁停风机,而不单是排烟风机入口处的排烟防火阀?

11.3.5 下列部位应设置排烟防火阀,排烟防火阀应具有在280℃时自行关闭和联锁关闭相应排烟风机、补风机的功能:     1 垂直主排烟管道与每层水平排烟管道连接处的水平管段上;     2 一个排烟系统负担多个防烟分区的排烟支管上;     3 排烟风机入口处;     4 排烟管道穿越防火分区处。

奋斗的样子 | 2024-10-11 23:18
请写下您的回答回答
הההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההההה
XXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXXX
输入一些内容
字符数: 0
单词数: 0


回答 | 5

STON 2024-10-12 08:48 00 [回复]举报

是的,温度到了280,都要连锁风机,防止高温烟气串到其他防烟分区,个人理解,仅供参考。

潘天坤 2024-10-12 11:58 00 [回复]举报

是连锁还是联锁,逻辑是怎么样的,有一定的争议

从文字理解,个人觉得:其他位置的排烟防火阀(除风机入口位置)需要达到“关闭后联锁关闭相应排烟风机、补风机的功能”

目前有一些做法报警主机编写逻辑,当接收到排烟防火阀的关闭信号后,停止风机,不过从电气逻辑来说可能有点问题,不知道后续会不会有更好的方案

建议楼主多与区域内设计、审查及验收专家交流,具体以他们意见为准
上述为根据国家规范的个人理解,不一定正确,有些地区技术文件可能有特别规定,建议结合地区技术文件和地区设计、审查、验收专家们的意见综合考虑


我头发贼黑 2024-10-12 15:18 00 [回复]举报

可以认为在这四个位置上的排烟防火阀关闭要连锁:

1 垂直主排烟管道与每层水平排烟管道连接处的水平管段上;

2 一个排烟系统负担多个防烟分区的排烟支管上;    

3 排烟风机入口处;    

4 排烟管道穿越防火分区处。

wetom 2024-10-12 16:36 10 [回复]举报

是的,设施通规的实施指南也说的很明确,在火灾时,烟气流经管路上的任一排烟防火阀在280℃关闭后,均应能联锁相关风机停止运行,防止系统管道内产生负压而被破坏。

仓鼠 2025-04-26 12:01 10 [回复]举报

我个人人为其实这个要思考火灾现场情况
第一点是:如果这个地方能到达280℃,说明火灾已经蔓延的,你二楼着火然后持续连锁关闭了风机,如果他已经蔓延到了三楼,难道三楼就不用风机了吗?
第二点是:能让火灾蔓延到这种程度这个时间是否还有人员滞留,关闭风机是不是也可以。
第三点是:风机入口处与支管上的排烟防火阀这两个的作用是不一样的,风机入口处的是防止到达280℃这种已经带有火焰的烟气损毁风机,而且这里能到达这个温度继续排烟意义也不大了,所以关闭风机避免吸力破坏风管让烟气在机房处扩散,并且闭阀保护风机。
而主管至支管上的排烟防火阀这个阀是为了防止带火烟气从竖向快速蔓延用的,如果关闭了这种情况大概率蔓延到上一层那上一层就不能再用了因为这个是持续的连锁关闭状态,这种情况风机能继续运行是还存在意义的。
这个不能排除所有人都能快速逃离火场个人建议支管上不应连锁关闭风机。

关闭

关闭

手机APP下载